Author

Topic: .05 BTC bounty - act now! (Read 2160 times)

full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 31, 2014, 08:52:56 PM
#24
Each of the 3 distribution panels (208/120 breaker panels) would have a 225 amp main breaker, not one single 225A breaker on the 208V output of the transformer.

Transformers are sized to permit 100% of their rating therefore 278 Amps (100080 watts) of 208V is avaliable for the 3 distruibution panels to share depending on connected load at each panel. In theroy it would be possible to load up the distribution panels (even following the 80% rule) to exceed the 278A output of the transformer but doing so would cause the main transformer breaker to trip on overload.
Best to have a qualified electrician or electrical eng review your plans.


Trends

Always a good idea to get a review by an expert. Some transformers can be overloaded depending on their insulation class and ambient temperature.
member
Activity: 119
Merit: 10
December 31, 2014, 08:15:49 PM
#23
Each of the 3 distribution panels (208/120 breaker panels) would have a 225 amp main breaker, not one single 225A breaker on the 208V output of the transformer.

Transformers are sized to permit 100% of their rating therefore 278 Amps (100080 watts) of 208V is avaliable for the 3 distruibution panels to share depending on connected load at each panel. In theroy it would be possible to load up the distribution panels (even following the 80% rule) to exceed the 278A output of the transformer but doing so would cause the main transformer breaker to trip on overload.
Best to have a qualified electrician or electrical eng review your plans.


Trends
legendary
Activity: 2744
Merit: 1193
I don't believe in denial.
December 30, 2014, 01:44:20 PM
#22
[...]
Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
That's the job of the power supplies.

So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...?

And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?

I believe most people who read this thread will understand the context that the 100KW is the "at-the-wall" power consumption of the equipment, before any losses due to PSU inefficiencies or wiring losses downstream of the PDU.

Possibly, but some (like the OP, maybe) won't:

I am not that good when it comes to electrical matters.  

First person to tell me (correctly) how many watts this PDU can supply to mining equipment, wins the bounty:

http://www.ebay.com/itm/PDI-PDU-100-KVA-480v-x-208v-3-Panel-Manuifactured-2009-/121527983792?pt=US_Uninterruptible_Power_Supplies&hash=item1c4ba1deb0


donator
Activity: 1617
Merit: 1012
December 30, 2014, 01:39:27 PM
#21
[...]
Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
That's the job of the power supplies.

So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...?

And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?

I believe most people who read this thread will understand the context that the 100KW is the "at-the-wall" power consumption of the equipment, before any losses due to PSU inefficiencies or wiring losses downstream of the PDU.
legendary
Activity: 2744
Merit: 1193
I don't believe in denial.
December 30, 2014, 01:26:28 PM
#20
[...]
Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
That's the job of the power supplies.

So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...?

And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?
donator
Activity: 1617
Merit: 1012
December 30, 2014, 01:20:23 PM
#19
KVA is equivelent to KW?

I thought there was a conversion involved.....

It is actually

KW = KVA x (power factor)

but the power factor of modern switching power supplies with active PFC that you find in mining equipment is usually very close to 1.0, so most people don't bother to account for it.
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 30, 2014, 12:20:17 PM
#18
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it
http://www.rapidtables.com/calc/electric/power-calculator.htm

put in the volts output of 208 and amps max is the main breaker of 225amps
hope this helps

edit its not 3 phase as no power factor is listed in spec

First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral.

Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2).

Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...


That's the job of the power supplies.
legendary
Activity: 2744
Merit: 1193
I don't believe in denial.
December 30, 2014, 12:17:10 PM
#17
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it
http://www.rapidtables.com/calc/electric/power-calculator.htm

put in the volts output of 208 and amps max is the main breaker of 225amps
hope this helps

edit its not 3 phase as no power factor is listed in spec

First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral.

Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2).

Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 30, 2014, 11:26:05 AM
#16
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it
http://www.rapidtables.com/calc/electric/power-calculator.htm

put in the volts output of 208 and amps max is the main breaker of 225amps
hope this helps

edit its not 3 phase as no power factor is listed in spec

First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral.

Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2).
hero member
Activity: 616
Merit: 500
December 30, 2014, 06:13:56 AM
#15
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it
http://www.rapidtables.com/calc/electric/power-calculator.htm

put in the volts output of 208 and amps max is the main breaker of 225amps
hope this helps

edit its not 3 phase as no power factor is listed in spec
power factor has nothing to do with being 3 phase or 1 phase

https://en.wikipedia.org/wiki/Power_factor

Cheers
newbie
Activity: 42
Merit: 0
December 30, 2014, 12:57:50 AM
#14
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it
http://www.rapidtables.com/calc/electric/power-calculator.htm

put in the volts output of 208 and amps max is the main breaker of 225amps
hope this helps

edit its not 3 phase as no power factor is listed in spec
sr. member
Activity: 440
Merit: 250
December 29, 2014, 09:13:13 PM
#13
KVA is equivelent to KW?

I thought there was a conversion involved.....

not really. Watts = Volts x Amps -->    W=VA  ----->  KVA=KW

there is some discrepency depending on your voltage input/output and other factors, but 100KVA means about 208A of 480V input power. Safe practice dictates keeping full-time load at less than 80%

Manufactures generally advertise max potential in a perfect set up not constant supply, Klondike is correct.

Edit - - - - TrippLite has had to re name several of their 220 - 240 PDUs because nobody in their right mind will ramp them up to full marketed AMPs
legendary
Activity: 2128
Merit: 1005
ASIC Wannabe
December 29, 2014, 08:11:21 PM
#12
KVA is equivelent to KW?

I thought there was a conversion involved.....

not really. Watts = Volts x Amps -->    W=VA  ----->  KVA=KW

there is some discrepency depending on your voltage input/output and other factors, but 100KVA means about 208A of 480V input power. Safe practice dictates keeping full-time load at less than 80%
legendary
Activity: 1666
Merit: 1185
dogiecoin.com
December 29, 2014, 05:24:41 PM
#11


Well there goes the hash rate!
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 29, 2014, 02:29:31 PM
#10
KVA is equivelent to KW?

I thought there was a conversion involved.....

Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage.

Make sure to load each phase evenly otherwise you'll cause harmonics.

BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1


OK, you win. 

Coming your way. 

Got it, thanks! Feel free to PM me if you have any more questions. If you're trying to mine, I may be able to give you some pointers that can save you lots of money. Check out the mine we're building, link in my signature.
legendary
Activity: 2044
Merit: 1000
December 29, 2014, 02:24:43 PM
#9
KVA is equivelent to KW?

I thought there was a conversion involved.....

Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage.

Make sure to load each phase evenly otherwise you'll cause harmonics.

BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1


OK, you win. 

Coming your way. 
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 29, 2014, 02:17:55 PM
#8
KVA is equivelent to KW?

I thought there was a conversion involved.....

Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage.

Make sure to load each phase evenly otherwise you'll cause harmonics.

BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1
member
Activity: 65
Merit: 10
December 29, 2014, 02:16:58 PM
#7
120 volts at 278 amps is 33360 watts

That's another way to look at it, but you forgot it's 3 phase so 120*278*3 = 100080 watts = 100 kw

Sheesh thats insane  Shocked
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 29, 2014, 02:16:21 PM
#6
120 volts at 278 amps is 33360 watts

That's another way to look at it, but you forgot it's 3 phase so 120*278*3 = 100080 watts = 100 kw
legendary
Activity: 2744
Merit: 1193
I don't believe in denial.
December 29, 2014, 02:15:18 PM
#5
None,

It clearly states:
SPECIFICATION
OUTPUT
208/120 volts  

I don't know which miners you had in mind, but generally ASIC miners run at 10-12 volts...
member
Activity: 65
Merit: 10
December 29, 2014, 02:14:41 PM
#4
120 volts at 278 amps is 33360 watts
legendary
Activity: 2044
Merit: 1000
December 29, 2014, 02:13:30 PM
#3
KVA is equivelent to KW?

I thought there was a conversion involved.....
full member
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
December 29, 2014, 02:11:25 PM
#2
It's a 100 KVA which means 100KW. A little less actually because the transformer inside doesn't have a perfect power factor.

KVA is "apparent power" while KW is real power. Apparent power is what you would get in a perfect world with no lagging reactive power due to the transformer.

Check out this link: http://www.apcmedia.com/salestools/SADE-5TNQYF/SADE-5TNQYF_R1_EN.pdf?sdirect=true

We're not using PDUs in our data center, just transformer + panels. We have some pics on our website: http://www.asicspace.com/
legendary
Activity: 2044
Merit: 1000
December 29, 2014, 02:09:34 PM
#1
I am not that good when it comes to electrical matters. 

First person to tell me (correctly) how many watts this PDU can supply to mining equipment, wins the bounty:

http://www.ebay.com/itm/PDI-PDU-100-KVA-480v-x-208v-3-Panel-Manuifactured-2009-/121527983792?pt=US_Uninterruptible_Power_Supplies&hash=item1c4ba1deb0

Jump to: