Topic: Are your breakers warm or hot to touch ? (Read 188 times)

member
Activity: 70
Merit: 34
March 06, 2018, 12:40:49 AM
#7
The numbers shown in your original post do not look like measured data. I was guessing these were calculated values instead.

If you can, actually measure the voltage and the current and perhaps the circuit breaker and conductor temperatures. This information will help me determine if this should be a concern or not. Once I know some measured values, I can determine if this condition is typical or if you should be looking for other problems.

So a clamp on ammeter with volt meter and an IR temperature meter would be very useful.

Your description does have me concerned. "All my breakers get warm to hot to the touch" is a description that is abnormal. My first method of diagnosis is to touch things to feel how much heat exists. All my cords and breakers are just barely warm enough to feel any warmth if I really concentrate on it. If I ever feel more than that, I measure, double-check, inspect and test everything.

I'm guessing again the calculated current is based on the specs shown on Bitmain's site which can result in underestimation of current. Which will likely result in an overloaded circuit. If you have over 80% load on the circuit, it is overloaded by definition.

When you measure the current on the three phase breaker, please be sure to measure all the current going through each leg of the breaker. There are 3. Also measure the voltages between a-b, b-c and c-a. Three phase can be tricky. If you have 3 miners connected, one to each phase, the current per leg at the breaker needs to be known to understand the system loading.

Any 30A circuit loaded at only 21A should be very close to ambient temperature. It should be very difficult to feel any warmth on that circuit breaker. The mention you do feel warm to hot means something is not correct.



 



member
Activity: 111
Merit: 14
01010011 01000111 01001101
March 05, 2018, 07:48:37 AM
#6
As long as they are not getting  extremely hot you should be okay.

Electricity generates heat no matter what so warm shouldn't be a problem. Honestly I don't really check mine unless I get a tripped breaker. If your confident enough you could open up the panel and look for signs of wear/burning

I use a clamp-on type amp meter - you can find these on Amazon or at any good hardware store.
legendary
Activity: 1554
Merit: 2037
March 04, 2018, 09:04:25 PM
#5
As long as they are not getting  extremely hot you should be okay.

Electricity generates heat no matter what so warm shouldn't be a problem. Honestly I don't really check mine unless I get a tripped breaker. If your confident enough you could open up the panel and look for signs of wear/burning
member
Activity: 70
Merit: 34
March 04, 2018, 08:32:51 PM
#4
May I ask how you measured the current on your breakers?
jr. member
Activity: 52
Merit: 1
March 04, 2018, 01:30:47 PM
#3
Yeah I think some heat is normal.  If they are not breaking you should be fine.  I have power filter light bars on my rigs and they are warm to the touch all of the time. 
member
Activity: 111
Merit: 14
01010011 01000111 01001101
March 04, 2018, 01:22:59 PM
#2
Breakers will get warm to the touch when they have a high load. Google the topic, there is a lot of stuff related to warm breakers.
newbie
Activity: 42
Merit: 0
March 04, 2018, 07:36:58 AM
#1
All my breakers get warm/hot to touch

24A @ 240V on a 30A breaker (single phase)

21A @ 208V on a 30A breaker (3 phase)

Both are continous load and on 80%. But they sure do get warm to hot sometimes.