Do you have a wattmeter plug?
Will that Whatmeter read the inrush current? I can't tell for sure but I highly doubt it.
I think the inrush current for the old power supplies like the APW3 and APW7 is <= 80 amps, it's safe to assume that it's a lot higher on the S17, however, the inrush current is so fast for most fuses/breakers to act upon, if inrush current was the issue then S9 would have caused the same issue, the problem here seems to be the 10A fuse itself, you are passing it a lot, the S17 consumes about 2100w so on a 220v it draws 9.5A, the slightest drop in voltage will take it above 10A, you need 9.5*1.35 = 12A or nearest to safely run an S17, for the S15 it does about 7.5A so I think a 10A will do the job as long as the voltage doesn't drop below 220v, if it does, it will blow, you need to measure your voltage and get the lowest number and judge based on that.