Hire a licensed Electrician to look things over.

Assuming 208V and a safe 1,500w per miner * 14 = 21kW = 101A total so *should be good. Since there is something major screwy there...

This is NOT something for DIY or 3rd-party remote guessing!

yeah you are 3 phase  so loads must be balanced

1+2
1+3
2+3

are the combos of the three phases

so  the most  load any can do is 66.6 x .8 = 53.28 amps

so

1+2 < 53 amps
1+3 < 53 amps
2+3 < 53 amps

but also balanced

so if the gear is 102 amps  what is all your other shit  say 30 amps

that is 132 amps of your 160 amp 80% derate

you are going to need some one with meters to see what each leg is doing
and to see if you are close to balanced.

can't fix via the forum

When we ran the meter all three legs were very close to balanced. Are they to be exact?

I had one electrician come and he figured it is a bad neutral connection, checked with the city so now I will be checking the shop side as well. I was hoping to run another 8 miners out of here. Each miner is essentially pulling 6.3 amps as I am on 220v. Which at 20 miners I should only be pulling 126 plus the other shit.  

There is no way I can't pull what I am pulling - right now as I have 6 Avalon 741s running on 110v 60Amp panel at my home and they don't miss a beat. Any thoughts on the PSUs as this is my first time using these?? - my home miners are on EVGA 1300 Golds.

I am in a pretty big industrial area so I have to assume the power supply from the city is fine. It seems mostly like I am getting surges, as some of my other electronics have started acting weird that aren't on UPS systems.

Will update when the problem is solved.

Thanks All.

 
newbie
Activity: 54
Merit: 0
October 11, 2017, 11:28:12 PM
#5
Its always important to acknowledge electrical reasons for the stake of the region capacity. Its always important to have everything on recordwhen it comes to these minig issues.
member
Activity: 67
Merit: 10
October 11, 2017, 09:08:41 PM
#4
Maybe you have unbalanced load or poor grounding. If not.. check if all are screws in the breakers are tight
legendary
Activity: 4326
Merit: 8950
'The right to privacy matters'
October 11, 2017, 07:59:45 PM
#3
Hire a licensed Electrician to look things over.

Assuming 208V and a safe 1,500w per miner * 14 = 21kW = 101A total so *should be good. Since there is something major screwy there...

This is NOT something for DIY or 3rd-party remote guessing!

yeah you are 3 phase  so loads must be balanced

1+2
1+3
2+3

are the combos of the three phases

so  the most  load any can do is 66.6 x .8 = 53.28 amps

so

1+2 < 53 amps
1+3 < 53 amps
2+3 < 53 amps

but also balanced

so if the gear is 102 amps  what is all your other shit  say 30 amps

that is 132 amps of your 160 amp 80% derate

you are going to need some one with meters to see what each leg is doing
and to see if you are close to balanced.

can't fix via the forum
legendary
Activity: 3822
Merit: 2703
Evil beware: We have waffles!
October 11, 2017, 07:05:31 PM
#2
Hire a licensed Electrician to look things over.

Assuming 208V and a safe 1,500w per miner * 14 = 21kW = 101A total so *should be good. Since there is something major screwy there...

This is NOT something for DIY or 3rd-party remote guessing!
newbie
Activity: 7
Merit: 0
October 11, 2017, 06:27:10 PM
#1
Hi Guys,

Hoping someone could help with an issues I am having.

I have a three phase 200amp service in my shop and I am getting electrical interruptions or surges when I power my miners on. Here is the setup:

I have 5 2 pole 40amp (220) breakers in which I was aiming to power two  http://www.parallelminer.com/product/delta-2400watt-power-supply-platinum-94-200-240v-dps-2400ab/ and four Avalon 741 on each.

My total current set up is 12 Avalon 741s and two Antminer L3s.

The issue I am having is when everything is powered on or even 3/4 are powered on I get lights flickering, computer UPS buzzing, outside lights buzzing.

I have had my city check the neutral line, as to me it seems like everything is drawing more power because the miners are or the neutral isn't letting power back. I am at a loss as they said everything is fine. Any opinions are welcomed?

Thanks in advance. 