Author

Topic: Mining room cooling - How much airflow for 20kW? (Read 384 times)

copper member
Activity: 30
Merit: 0
If this calculation for one m3 for 20kw ?


https://www.engineeringtoolbox.com/cooling-heating-equations-d_747.html

hs = cp ρ q dt

hs= 20 kW
cp = specific heat of air (1.006 kJ/kg C)
ρ = density of air (1.202 kg/m3)
q = 2000/3600=0.555555
dt = temperature difference (C)

So with 20kW that airflow will see a delta T of 20/(1.006*1.202*0.55555)=29.8 C

Lets take a real cool ambient temp of 20C, that would mean that the air exiting will be 60C, and you cards will then most probably will be running at 80+C.

Double the Air flow and the deltaT will be reduced to half, with exit T of 45C, a much better situation.
The math is actually really simple when you reduce the situation to total air flow and total power inserted to the system.

With very controlled airflow (so all cards get the ambient air and no exhaust from another card) the cards will see a lower peak. Water cooling would be even better to control where the heat goes. But the heat transfer by air is till the same, 20kW transferred to 2000 m3/h air gives deltaT of 30C.
legendary
Activity: 4116
Merit: 7849
'The right to privacy matters'
I’d use the whole room for 80% cold/intake air - and isolate the hot side at the exhaust fan

this is the way to go.

jr. member
Activity: 306
Merit: 7
No way I invest in an AC for that room  Grin
sr. member
Activity: 847
Merit: 383
I am a AC guy. 

Here is the calc if you want to cool the place.  (I would not, but some do.)
Total watts x 3.14 BTU / 12,000 = Total Tonnage

Example
20K watts x 3.14 = 62,800 / 12,000 = 5.23 tons of air will do it without ventilation.  So 6 Tons counting room etc would suffice to keep that beast about 72 F
jr. member
Activity: 306
Merit: 7
I have to say, that I have to spend some more time understanding the physics of heat.
But would you say, I will have to change the ventilator for my room i described in the first post?
Its something I have, so i mighr give it a try. Since my rigs are splitted at 3 locations. 2 of the locations are just ventilated by open windows  Tongue
newbie
Activity: 56
Merit: 0
My next task to do when it starts to cool off is to have both fans work off the thermostat and have a simple 1 way flap above it so when one is on it will not draw from the other one.

I'll most likely set them at 80F and 100F or something like that.

https://quietcoolsystems.com/ makes an extremely efficient variable fan which would be totally awesome.

https://www.amazon.com/Quietcool-Attic-Gable-Ventilation-Exhaust/dp/B073ZNGR6S
newbie
Activity: 56
Merit: 0
23 / (1.006 * 1.202 * (10194.064774 / 3600) ) = 6.7 C = 44F
Keep track of your imperial units.
T(°F) = T(°C) × 9/5 + 32

So a delta T of 6.7C is the same as a delta T of 12F, the 32 is just an offset for when the two scales are zero.

Thanks,

It works perfect then!! Exactly what I see. I'm guessing I really dont get all 6000 cfm out of the fans. I but its more like 5000 after advertising and having to pull through the filters.

Thanks again.
jr. member
Activity: 94
Merit: 1
23 / (1.006 * 1.202 * (10194.064774 / 3600) ) = 6.7 C = 44F
Keep track of your imperial units.
T(°F) = T(°C) × 9/5 + 32

So a delta T of 6.7C is the same as a delta T of 12F, the 32 is just an offset for when the two scales are zero.
newbie
Activity: 56
Merit: 0
23 / (1.006 * 1.202 * (10194.064774 / 3600) ) = 6.7 C = 44F

Something doesn't seam right. That is about 3 times what I see. Is it because not all the kW is converted to heat?

Those are my calculations and I don't see anywhere near 44F delta.


Example - Heating Air
An air flow of one cfm is heated from 32 to 52oF. Using (1) the sensible heat added to the air can be expressed as:

hs = 1.08 (1 cfm) ((52 oF) - (32 oF))      

    = 21.6 (Btu/hr)

this one works for me.

1.08 *  5000 * (100-94)
legendary
Activity: 1638
Merit: 1046
The important is you must take out the hot air on the room, adding an exhaust fan or seperate the miners with duct host in the exhaust fan to push the air out from the room.

This is just a sample image below
Sample image.
jr. member
Activity: 94
Merit: 1
https://www.engineeringtoolbox.com/cooling-heating-equations-d_747.html

hs = cp ρ q dt

hs= 20 kW
cp = specific heat of air (1.006 kJ/kg C)
ρ = density of air (1.202 kg/m3)
q = 2000/3600=0.555555
dt = temperature difference (C)

So with 20kW that airflow will see a delta T of 20/(1.006*1.202*0.55555)=29.8 C

Lets take a real cool ambient temp of 20C, that would mean that the air exiting will be 60C, and you cards will then most probably will be running at 80+C.

Double the Air flow and the deltaT will be reduced to half, with exit T of 45C, a much better situation.
The math is actually really simple when you reduce the situation to total air flow and total power inserted to the system.

With very controlled airflow (so all cards get the ambient air and no exhaust from another card) the cards will see a lower peak. Water cooling would be even better to control where the heat goes. But the heat transfer by air is till the same, 20kW transferred to 2000 m3/h air gives deltaT of 30C.
member
Activity: 277
Merit: 23
If you wanna use the entire room you will need at least 40 air change per hour, if you can add another fan for intake on the other side of room that should do it....

But i like TheRealCashen  design, I might try this for couple of ASIC
newbie
Activity: 56
Merit: 0
Hi guys,

I have a cold basement room. It has a window, in which a ventilator is installed, that pushes 2000m3 per hour out through a short pipe and gets fresh air through an opening from outside.

The room has 90m3. But I can downsize it to 30m3.

Will 20kW of miners and some ASICs work with that ventilator?
Should I downsize the room to exchange the hotter air faster or leave it big, so it can distribute?

Thank you in advance!

I love this topic.

I use 2 x ~3Kcfm fans for my 23kW cabinet. Works awesome. You do not need cold air. You need a lot of flow and that flow needs to actually transfer the heat and move the heat away from the equipment.

I'll NEVER use anything again besides this cabinet design. Its amazing. No noise, no heat, all contained.

I have a large screened window open in my garage which pulls outside air into my garage, filters it through the box, exhausts the hot air into the attic and then vents back to outside. I have never seen the exhaust over 110 degrees. Which we have had plenty of 100 degree days here in Missouri.

Good luck



https://twitter.com/CryptoLily/status/1011036351268081664

Quote
copper member
Activity: 96
Merit: 1
I’d use the whole room for 80% cold/intake air - and isolate the hot side at the exhaust fan
jr. member
Activity: 306
Merit: 7
Hi guys,

I have a cold basement room. It has a window, in which a ventilator is installed, that pushes 2000m3 per hour out through a short pipe and gets fresh air through an opening from outside.

The room has 90m3. But I can downsize it to 30m3.

Will 20kW of miners and some ASICs work with that ventilator?
Should I downsize the room to exchange the hotter air faster or leave it big, so it can distribute?

Thank you in advance!
Jump to: