Topic: Running 4x S9 on a 30A breaker + wiring + APC AP9571A 30a 208V PDU (Read 171 times)

newbie
Activity: 42
Merit: 0
On the wall, the S9's can go upto 1500 watts. That will be above the 80% rule at 208 volt. Do you have any taps on the transformer to increase the voltage? Thanks.


no, i dont have taps, could you explain on how that would help ?  Thanks !!
hero member
Activity: 756
Merit: 560
4 on a 30amp breaker is just fine. I even have a few dozen 30amp breakers running 5 altho in the summer the breakers trip from the heat and over use. I wouldnt recommend more than 4.
full member
Activity: 210
Merit: 100
On the wall, the S9's can go upto 1500 watts. That will be above the 80% rule at 208 volt. Do you have any taps on the transformer to increase the voltage? Thanks.
newbie
Activity: 42
Merit: 0
Is this setup safe ? running borderline at about 80% capacity