Hi, I'm helping someone build a smaller mining farm and the capacity for the electricity will be 30kW.
According to this video by Block Operations
https://www.youtube.com/watch?v=D7e-bKDFidk for each miner we need 200 cfm of airflow, which is equal to 340 m3/h and a total of 4000 cfm. To start with, does that make sense if a rig produces around 1500w? For this we would have 20 rigs.
Here's an drawing of what it will look like:
Here's the plan:
- 4-6 shelves (The pink boxes in the image).
- 3-4 rigs on each shelf
- Air intake on the floor, which basically is a raised floor, with a 20x50 cm (8x20") hole that blows air from an intake. Each vent will be 0.1m2.
- Each rig will be 8xGPU, about 80cm wide, with 7 Delta fans (0.8A, 113 CFM) on each, blowing a total of 791 CFM air per rig into the middle of the room.
- Intake fan is 500mm (20"), pushing 5800 cfm at max, taking air from outside with a dust filter
- Exhaust fan is 500mm (20"), pushing 5800 cfm at max
- The fans can be regulated according to the outside temperature
So the flow is cool air from outside, to each rig, out into the room, and out of the room.
At the end of the room (top in the drawing) will be an exhaust fan, moving the air out of the room, and to the outside, through the roof or front of the building.
So the questions are:
1) Will the air from the floor vents be equally distributed so all rigs get cool air? Or is there any better option? Would a continuous vent along wall like 300x20cm (120x8") be better?
2) What's the best location for the exhaust fan, to make sure all rigs are cooled equally. Now that I think of it, centered in the room might be better. Or would two fans be better?
3) Would it be better to just have an intake fan in the bottom of the room (where it says 3.4) and make a wind tunnel through the room? Where would the rig fans get their air from in that case? Some kind of turbulence?
4) With 500mm (20") vents connected to the fans, the area of the vent is 0.2m2, so I'm considering if this should be equal to the floor vents, but I'm not sure.
5) Is 200 cfm per rig adequate and would each fan need to move 2000 cfm each? Which means I basically can triple the power consumption and still move the hot air out if the fans are on max?
6) Does the size of the room matter? Would it be better to have it less wide?
I'm looking forward to hear your thoughts on this. If you have a lot of experience in building farms with direct air cooling, and can consult me on this by email, PM me and we can discuss a reward.
Thanks!
I did mine with around 20kw. I am not sure what i am looking at exactly in your drawing.
I hope u realize that the sound will be VERY LOUD. U can hear it even 15-20 meters away.
Tips:
Shelves - use good shelves shelves that can take over 100kg, not those ikea shelves with 32-40kg max load weight.
Your air intake and exhaust - MAKE SURE the exhaust HOT air does not recirculate into the AIR INTAKE in any situation. Meaning the hot air that goes out does not get to back into the intake if the wind blows a certain way. Account for the fact that wind changes and put a good margin of safety on this.
Airflow - U dont need air intake. As long as the room is sealed and air is pushed outside the room, air will automatically enter the room through any opening. The amount it pushes air out depends on the pascal air pressure in the room. Mine is around 200 pascal via box fan, something like page 280 here
http://rosenberg.com.sg/wp-content/uploads/2015/04/worldoffans_en-2.pdf . U can use any sort of fan though. In general, dont take air in from ground as the air is abit more dusty and since warm air rises, it is abit better to put air out-take/exhaust fan at higher point or at least middle.
Also six 0.1m2 holes is about 0.6m2 total. That may be too much. Your air pressure pascal might be too low. U may wanna get an engineer to calculate or perhaps start with smaller holes and widen them slowly.
Air dust filter - This is important but do note that it will slow down the air flow coming in a little depending on wat air filter type u put, be it G3/G4/etc filter.
Rain and air intake area - This is important. Since u have ALOT of airflow going in and out of your small room, u gotta make sure the air intake does not pull in water as well. I suggest having the direction of air coming in not point directly at your miners as it may bring some water in. For example, the intake air comes in through a duct that face downward to the ground, making the air come in facing downwards. This way, if any water droplets gets pulled in, it will drop to the floor. I suggest leave some distance between air intake and shelves. Same with exhaust, u may need to push the air through a fan through a duct due to rain, depends on situation.
If u have the space and it is economical enough, u may want to split it into 3-4 exhaust fans rather than 2, so that if one fails, u still have 2-3 working. Alternatively, u may wanna try get an electrician to use control circuitry with your box fans (if your box fan has that function), to wire it to the distribution box such that if the box fan fails, it shuts off the power at distribution box. This is because if box fan fails, your machines will overheat and the miner goes into overheat protection mode which works fine but I juz rather avoid. However, not all electricians know how to do this, juz fyi. May cost abit also.
Electrical -
Best to use power factor of 0.8 - 0.85.
Since it is on 24/7, this is continuous load, do not put more than 80% load on a breaker. Meaning if it is 20amp breaker, put at most 16 amp on it. Same with each socket, best to put more sockets and dont overload.
Make sure your wires are all good copper wires that are big enough. U dont want them overheating.
Use good mcb like hager or MK. Dont use cheap china mcb which may cause issues.
I use a surge arrestor for the distribution box to prevent surges. U may want one.