Well this is what I wanna do before I get more confused, I have a warehouse with a panels that has a 3 phase 208v layout. I have 6 cointerras ready to be plug in but i wanna switch to 240 so I can be a bit more efficient. what do i do?

Unless the utility offers 240V there (which is doubtful), you can't.  Okay, you could get boost transformers to convert to 240V, but the loss in the transformers would negate any small efficiency gain you might get in the downstream power supplies.  Have you examined the efficiency curves for the supplies to see what the efficiency difference would be?
member
Activity: 90
Merit: 10
3 phase (208V single phase is unusual, if not nonexistent).

208V single phase PDU is very common.   A single 3 phase drop is split into three 1 phase drops and a single phase PDU used for each one.   In a datacenter usually racks are 30A or less so it allows you to power three racks using a single drop and three PDUs.

Well this is what I wanna do before I get more confused, I have a warehouse with a panels that has a 3 phase 208v layout. I have 6 cointerras ready to be plug in but i wanna switch to 240 so I can be a bit more efficient. what do i do?
donator
Activity: 1218
Merit: 1079
Gerald Davis
Should have said 208V single phase from the utility is unusual if not nonexistent.

Gotcha.  Yeah that would be unusual.
newbie
Activity: 3
Merit: 0
3 phase (208V single phase is unusual, if not nonexistent).

208V single phase PDU is very common.   A single 3 phase drop is split into three 1 phase drops and a single phase PDU used for each one.   In a datacenter usually racks are 30A or less so it allows you to power three racks using a single drop and three PDUs.

Should have said 208V single phase from the utility is unusual if not nonexistent.  Certainly the premises can then be wired with 208V 3-phase circuits, 208V 1-phase circuits, and 120V 1-phase circuits.
donator
Activity: 1218
Merit: 1079
Gerald Davis
3 phase (208V single phase is unusual, if not nonexistent).

208V single phase PDU is very common.   A single 3 phase drop is split into three 1 phase drops and a single phase PDU used for each one.   In a datacenter usually racks are 30A or less so it allows you to power three racks using a single drop and three PDUs.
member
Activity: 90
Merit: 10
Well Im looking to set 5 cointerra miners at a shop using 208 v, some I was looking to get a PDU3VN10G60 which supposedly can feed up to 12600 watts but then when I was reading the specs says that I will only take 35 amps of input.

here is the link

http://www.tripplite.com/sku/PDU3VN10G60/

Can anybody explain to me how this works?? How will I ever put 12600 watts on a PDU that can only take 35 amps??

I would really appreciate any feedback, thanks.

Nico
It is a 3-phase device. Maximum output current is in each phase is 20A. 3*20A*208V=12480W.

Basic introduction to 3-phase systems:

http://en.wikipedia.org/wiki/Three-phase
http://en.wikipedia.org/wiki/Three-phase_electric_power



5 Terraminers have 10 power cords, each drawing 2100W/2/210V = 5A.

You can't distribute them evenly amongst 3 phases. The closest is 3+3+4. So it will be drawing 15A+15A+20A. One circuit is at its maximum. Any further asymmetry and they will start tripping the breakers.

It could work if all the Terraminers have perfect power supplies with perfect load sequencing.


I think Im just gonna buy 3 of this ones

Tripp Lite PDUMV30HV Metered 208/240V 30A 10 ft PDU

http://www.newegg.com/Product/Product.aspx?gclid=CNCZ9MuNr74CFYFQOgodtRsAzg&Item=N82E16812120338&nm_mc=KNC-GoogleAdwords&cm_mmc=KNC-GoogleAdwords-_-pla-_-Power+Distribution+Unit-_-N82E16812120338&ef_id=U27rvwAABTlJ2oNO:20140515234229:s
donator
Activity: 1218
Merit: 1079
Gerald Davis
As pointed out that is a 3 phase device.  Unless your premises is wired for 3 phase power that PDU is useless.   If you don't know then it isn't.
legendary
Activity: 2128
Merit: 1073
Well Im looking to set 5 cointerra miners at a shop using 208 v, some I was looking to get a PDU3VN10G60 which supposedly can feed up to 12600 watts but then when I was reading the specs says that I will only take 35 amps of input.

here is the link

http://www.tripplite.com/sku/PDU3VN10G60/

Can anybody explain to me how this works?? How will I ever put 12600 watts on a PDU that can only take 35 amps??

I would really appreciate any feedback, thanks.

Nico
It is a 3-phase device. Maximum output current is in each phase is 20A. 3*20A*208V=12480W.

Basic introduction to 3-phase systems:

http://en.wikipedia.org/wiki/Three-phase
http://en.wikipedia.org/wiki/Three-phase_electric_power

5 Terraminers have 10 power cords, each drawing 2100W/2/210V = 5A.

You can't distribute them evenly amongst 3 phases. The closest is 3+3+4. So it will be drawing 15A+15A+20A. One circuit is at its maximum. Any further asymmetry and they will start tripping the breakers.

It could work if all the Terraminers have perfect power supplies with perfect load sequencing.
newbie
Activity: 3
Merit: 0
3 phase (208V single phase is unusual, if not nonexistent).

35A * 208V * sqrt(3) = 12600W
member
Activity: 90
Merit: 10
Well Im looking to set 5 cointerra miners at a shop using 208 v, some I was looking to get a PDU3VN10G60 which supposedly can feed up to 12600 watts but then when I was reading the specs says that I will only take 35 amps of input.

here is the link

http://www.tripplite.com/sku/PDU3VN10G60/

Can anybody explain to me how this works?? How will I ever put 12600 watts on a PDU that can only take 35 amps??

I would really appreciate any feedback, thanks.

Nico

P(power) = I(current) x E(voltage)

12600(w)/35(amps) = 360v

the specs says 12.6 kWatts / 208 Volts / then its says 60 amps output but 35 input??

hero member
Activity: 966
Merit: 513
Well Im looking to set 5 cointerra miners at a shop using 208 v, some I was looking to get a PDU3VN10G60 which supposedly can feed up to 12600 watts but then when I was reading the specs says that I will only take 35 amps of input.

here is the link

http://www.tripplite.com/sku/PDU3VN10G60/

Can anybody explain to me how this works?? How will I ever put 12600 watts on a PDU that can only take 35 amps??

I would really appreciate any feedback, thanks.

Nico

P(power) = I(current) x E(voltage)

12600(w)/35(amps) = 360v
member
Activity: 90
Merit: 10
then why do they advertise 12600 watts ??
hero member
Activity: 756
Merit: 501
You can't.

You will need 2 30 amp 208V circuits to power those 5 machines.  And a lot of cooling capacity.
member
Activity: 90
Merit: 10
Well Im looking to set 5 cointerra miners at a shop using 208 v, some I was looking to get a PDU3VN10G60 which supposedly can feed up to 12600 watts but then when I was reading the specs says that I will only take 35 amps of input.

here is the link

http://www.tripplite.com/sku/PDU3VN10G60/

Can anybody explain to me how this works?? How will I ever put 12600 watts on a PDU that can only take 35 amps??

I would really appreciate any feedback, thanks.

Nico
Pages:
Jump to: