Power is the same regardless of delta or Wye.
From the end user view the main difference is having one wild leg that is only a 220v power feed and a neutral at the center of one winding for 110v from it to the other 2 legs. Yes you have three phase power but the loading is very unbalanced whereas a wye will give 220 across each of the 3 legs and/or 110v from any leg to the center-point neutral.

Assuming a balance load 3-phase equation is V*average current of the 3 legs (or just pick the highest current one)*1.73= Watts
ref https://en.wikipedia.org/wiki/Three-phase_electric_power
member
Activity: 113
Merit: 31
I've got a question regarding Delta vs WYE 3 Phase service.  

If I understand WYE correctly with 200amp 120/208 service, that would give me 208V x 200A x 1.732 = ~72kW available power.  Each hot leg would be 120V x 200A = 24kW x3 legs = 72kW.

Can someone tell me how that equation works out for Delta service?  I have 240 volts between each of the phases, 120 volts to ground on 2 legs, and 208 volts to ground on 1 leg.  Is the equation 120V x 200A x 2 + 208V x 200A? That equals 48kW + 41.6kW = 89.6kW when adding the phases separately?  How does that translate to 3 phases when trying to calculate total kW?

Unfortunately the building where I'm at has Delta 3 Phase so I'm trying to understand how much power is available with that service.

I appreciate any feedback and/or corrections of my calculations.