First thing i would have done it open the Main Breaker box and check what gauge the main wires were coming into from the outside wire
connection from the pole. You could easy calculate what amperage you have coming in and calculate how many rigs you can run without
changing anything major from the pole.
Say what? "You could easily calculate what amperage you have coming in"? The amount of current coming is totally dependent on what the load is. In this case the load would be rigs, lights, fans, etc. You cant have any current flow without a load.
A cheap harbor freight infrared thermometer is your friend. Check all connection with the IR Thermometer. If one is loose then its temperature will be 5-10 degrees plus higher than the rest. This check can only be performed when there are loads connected to the breaker panel. (AKA branch circuits connected to your (branch) circuit breakers. Use proper electrical safety when working in an electrical panel at all times!
OP....You just call the power company that feeds power to the building and ask them what the service entrance feed from the pole is rated for. Goto your main panel and check the main breaker rating and take that number and multiply that by your service voltage and that answer will be your total watts. Your main panel will tell you what your voltage is most likely if all the stickers are still there. Then multiply total watts by .80 (80%) which is the 20% derating amount for constant duty cycle.
Heres an example for a typical U.S. household.
200amp main breaker 240vac service entrance feed.
200 x 240 = 48000 watts.
48000 x .80 = 38400 watts Total Watts available for constant Duty Cycle.
Do not think you will use a power cable to feed equipment that is rated for say 20amps and think it will be ok to run 18Amps continuously 24/7. Remember the 80% rule of derating for constant duty cycle.
Basic electrical math formulas
Power (w) = E (volts) x I (Amps) P=ExI
E (volts) = Power (w) / I (Amps) E=P/I
I (amps) = Power (w) / E (volts) I=P/E
I=Current P=Power E=Voltage
Now there is also a possibility that this warehouse has 3 phase power and thats a whole different ballgame. Could be 208 3 phase, 480 3 phase and even bigger depending on what the building was used for over the years. You should have checked to see what the power input to the building was before you leased it. If its 3 phase then you are screwed because you will need alot of step down transformers and your efficiency will be down in the weeds. 208 3 phase is 120v to ground from each leg to ground. You cannot get 240v from 208 3 phase without very expensive step up transformers.