The dismantling of the air conditioner may seem relatively simple, but it is only at first glance. To disassemble the inverter or split-non-inverter air conditioner, you need to follow several rules and specific tools. It helps a lot when cleaning with https://www.airconservicingsingapore.com/chemical-overhaul/ / It is imperative to understand that the entire air conditioner is not dismantled system correctly may be damaged, and in this case, it will simply stop working. Did you do air conditioning cleaning?
member
Activity: 108
Merit: 11
Im not an expert by no means but couldnt you cool air in another room, have the mining room have a powerful extraction fan to vent the heat, then have cool air passively "sucked" into the hot room?
hero member
Activity: 812
Merit: 500
I have open my computer case and this great cooling.
newbie
Activity: 51
Merit: 0
Guys, I'm a mid size miner (i Have 250 rigs) I also own a HVAC company.  I have survived 3 years of Texas summers where ambient is 105.  The key and I can not stress this enough is ventilation.  The more the better.  Don't be stupid and add 1 box fan for 10 units on the window.  Buy a 3000 cfm or bigger unit.  Put it this way, I have 30 units in one location that is 130 square feet and air-flowing from attic and pumping out through window at a rate of 9000 cfm.  Its a vortex in there to battle the Texas heat.  Is cooling it better?  Absolutely but the cost incurred is great, plus it takes 50 amps of mining away.

Calculation is this.

say you have 10 machines doing 1200 watts
10 x 1200 = 12000 watts
12000 x 3.41 (btu per watt) = 40,920 BTU
40,920 / 12000 (12k btu per ton of air) = 3.41 Tons

So you will need 3.41 Tons of air to cool just the machines so in this case a 4 ton unit should be fine.

Hope that clears stuff up.

Just curious i have about 22 rig each rig is doing about 600-700watt
22X700 =15400watt
15400 wattX 3.41 = 52514 BTU
53000BTU /24000(assume i buy aircon with 24kBTU) = so does that mean 2 such aircon is enough or maybe i add to 3 of such aircon?

I know alot will say is a waste but currently using ventilation cause alot of noise which i still think to run with aircon is it possible


yvmen
newbie
Activity: 50
Merit: 0
I'm going for one of these when the outdoor temps start getting warmer here ...
https://www.amazon.com/AirKing-9166-Whole-House-Window/dp/B0007Q3RQ6
I know what is there on the market, that thing is 3000CFM, for sure it gonna blow like a hell, but again if you have a 1000 GPU it wont be enough.

So my questing is to how to calculate required CFM based on BTU/ACH.
member
Activity: 644
Merit: 24
I'm going for one of these when the outdoor temps start getting warmer here ...

https://www.amazon.com/AirKing-9166-Whole-House-Window/dp/B0007Q3RQ6
newbie
Activity: 50
Merit: 0
You divided by 60
What do you mean? This is how you get CFM (Cubic Feet per Minute). RCFM = Volume * ACH / 60.
legendary
Activity: 4256
Merit: 8551
'The right to privacy matters'
I am trying to calculate the required CFM (RCFM) for the area 10x5x6 with 7kW of power in it.
My calculations are:
V = 10x5x6 = 300 ft3.
BTU = 7000x3.41 = 23870
Air changes per hour (ACH) in data centers is suggested to be 50, so
RCFM = 300x50/60 = 250CFM

The problem here that 50 ACH I found in some guides "how to build a data center", so there was no really explanation where this number comes from.
I think ACH should be calculated somehow with using BTU.
And second of all 250CFM doesn't seem enough for 300 ft3 and 7kW.

Any advise if my calculations are correct and how to connect CFM with BTU please?
 


You divided by 60
newbie
Activity: 50
Merit: 0
I am trying to calculate the required CFM (RCFM) for the area 10'x5'x6' with 7kW of power in it.
My calculations are:
V = 10x5x6 = 300 ft3.
BTU = 7000x3.41 = 23870
Air changes per hour (ACH) in data centers is suggested to be 50, so
RCFM = 300x50/60 = 250CFM

The problem here that 50 ACH I found in some guides "how to build a data center", so there was no really explanation where this number comes from.
I think ACH should be calculated somehow with using BTU.
And second of all 250CFM doesn't seem enough for 300 ft3 and 7kW.

Any advise if my calculations are correct and how to connect CFM with BTU please?
 
full member
Activity: 686
Merit: 140
Linux FOREVER! Resistance is futile!!!
Air intake and exhaust vent capacities should be designed to be equal, or very close to it.
If you are using fans on the intake, a HAIR higher on the intake side will tend to cause a slight amount of positive pressure in the room which keeps dust/pollen/etc. infiltration to a minimum from anything that isn't specifically designed to be a vent.

This is how most "old school" data centers were designed, and the "new school" stuff like the Yahoo "chicken coop" design is even MORE of a "positive pressure" design.

 Don't use fans for BOTH intake and exhaust though, that's a waste of power.
 Use fans on ONE side and size the venting for the other side to suit.

 The only reason to use both an intake AND an exhaust fan is if you are dealing with a high "backpressure" situation, an air path with a VERY congested airflow path - like the inside of an S7 or S9 miner.


Nice info, Thanks.

I'm using 2 outlet fans on one side of the room and put filters on the next side windows to filter out dust.
Also I put some pushing fans between windows and rigs to blow air to rigs.
Temp near the window before rigs is around 5 °C and near outlet fans is around 25 °C, outside temp is around 0 °C.
GPU temps are around 60-70 now.

I'm curious what will happen in summer when outside temp reaches 30 °C
Outside and inside temp difference is now 20~30 °C, then in summer room temp gonna go as high as 60 °C and GPU temps gonna reach 80 ...

Does pushing more air to the room gonna lower temp, or I should find another solution for the summer?
What are my other solutions?


I made some changes to the layout of the room and got very good results.
Open windows and puller fans were in cross walls and back of the rigs were on windows with pushing fans between rigs and windows,
I turned rigs 90° to the windows on the other side of the room facing the puller fans.
Now the air flow is direct, from windows to push fans to rigs to puller fans.

The result is amazing, outside temp is now 5° C and room temp is 10° C, while GPU temps are around 30-40° C.

So my suggestion to every one is to set your layout to have a direct air flow from outside to your rigs and then to pulling fans so the hot air won't circulate in room and directly gets out.
newbie
Activity: 6
Merit: 0
Guys, I'm a mid size miner (i Have 250 rigs) I also own a HVAC company.  I have survived 3 years of Texas summers where ambient is 105.  The key and I can not stress this enough is ventilation.  The more the better.  Don't be stupid and add 1 box fan for 10 units on the window.  Buy a 3000 cfm or bigger unit.  Put it this way, I have 30 units in one location that is 130 square feet and air-flowing from attic and pumping out through window at a rate of 9000 cfm.  Its a vortex in there to battle the Texas heat.  Is cooling it better?  Absolutely but the cost incurred is great, plus it takes 50 amps of mining away.

dagarair:  Thanks for the post, good stuff.  I'm curious what your thoughts are on airflow for a home "server room" in the Midwest (Northern Illinois).  Based on my prelim calculations, I probably won't need AC ever (middle of summer is iffy) to cool the room however I'm designing it now and my main concern is a large enough exhaust.  Since I have to open up my exterior wall (twice, for intake/exhaust), I'm trying not to make holes bigger than the width of the studs.  The room will have dimensions of 4' by 13.5' (54 sq ft).  My hot aisle airflow isn't ideal however it's not terrible either.  It will be semi-sealed with only an exhaust fan and (industrial grade?) filters on the intake (don't want critters/dust/etc in my server room).  I also need to manage the sound since I live in a residential area and my neighbor is 15' from the edge of my house...  I'd considered looking into exhaust designs to minimize the sound so all my neighbors don't hear it all day...

Any suggestions on an exhaust fan (CFM rating)?  I'm not asking you to endorse a specific product however I'm not opposed to some suggestions either. 

I almost forgot, my current design for that room will be generating 90k btu/Hr.  I'm working on a secondary room design that'll generate another 120k btu/Hr of heat, same question there and would love a suggestion on exhaust fan capacity.

I realize this is subjective since what one might feel is an adequately cool room will differ but it gives me somewhere to start.
newbie
Activity: 34
Merit: 0
If you have a free electricity you can do it, but keep in mind that many of AC's are burned down due too 24// working hours.
Something like central AC industrial standard is preferable.
full member
Activity: 434
Merit: 107
effective extraction > cooling air temp.

If you have both = winning
jr. member
Activity: 35
Merit: 1
Check Two Ton Hasher youtube channel

He lives in Florida (Can get very hot and humid during summer time/hurricane season)

https://www.youtube.com/watch?v=E-_9F8R_PFU

https://www.youtube.com/watch?v=_qbLkivgxps
legendary
Activity: 1498
Merit: 1030
More air flow would probably help a lot.
You could use an evap cooler pulling air in from the outside, or less efficiently from the "hot" side of the room, blowing cooler air into the "cool" side.
If you had to, you could use an A/C unit to put SOME cold air into the intake air, just don't expect it to get the intake air WAY down on temp but it might help a little.



I already have a 24000 A/C in room (not in use for now), but dont know if it could help when we pull warm outside air to the room in the summer or not.

I was actually thinking about evap/water cooling air conditioners too, but doesn't high humidity cause problem to mining rigs?
I have some of those at home, they raise my home humidity from 30% in winter to +60% in the summer when they are in use.

 I've never seen the output of my Evap coolers get *TO* 60% RH.
 Realistically though, electronic gear is normally specified to handle at least 80% and often 85-90% RH while operating - and given how HOT miners get internally, you could probably feed them ANY level of humidity at the input that doesn't have active condensation without issues.

 Then again, even WITH one evap in the mining area and a ultrasonic "small room humidifier" in the office area running right now, I'm only seeing 26% RH in my office area and 28% in the mining area, even though it has been intermittantly RAINING this morning.
full member
Activity: 686
Merit: 140
Linux FOREVER! Resistance is futile!!!
Guys, I'm a mid size miner (i Have 250 rigs) I also own a HVAC company.  I have survived 3 years of Texas summers where ambient is 105.  The key and I can not stress this enough is ventilation.  The more the better.  Don't be stupid and add 1 box fan for 10 units on the window.  Buy a 3000 cfm or bigger unit.  Put it this way, I have 30 units in one location that is 130 square feet and air-flowing from attic and pumping out through window at a rate of 9000 cfm.  Its a vortex in there to battle the Texas heat.  Is cooling it better?  Absolutely but the cost incurred is great, plus it takes 50 amps of mining away.

Calculation is this.

say you have 10 machines doing 1200 watts
10 x 1200 = 12000 watts
12000 x 3.41 (btu per watt) = 40,920 BTU
40,920 / 12000 (12k btu per ton of air) = 3.41 Tons

So you will need 3.41 Tons of air to cool just the machines so in this case a 4 ton unit should be fine.

Hope that clears stuff up.

Thanks a lot for the info.
Gonna add more and more fans Wink
sr. member
Activity: 847
Merit: 383
Guys, I'm a mid size miner (i Have 250 rigs) I also own a HVAC company.  I have survived 3 years of Texas summers where ambient is 105.  The key and I can not stress this enough is ventilation.  The more the better.  Don't be stupid and add 1 box fan for 10 units on the window.  Buy a 3000 cfm or bigger unit.  Put it this way, I have 30 units in one location that is 130 square feet and air-flowing from attic and pumping out through window at a rate of 9000 cfm.  Its a vortex in there to battle the Texas heat.  Is cooling it better?  Absolutely but the cost incurred is great, plus it takes 50 amps of mining away.

Calculation is this.

say you have 10 machines doing 1200 watts
10 x 1200 = 12000 watts
12000 x 3.41 (btu per watt) = 40,920 BTU
40,920 / 12000 (12k btu per ton of air) = 3.41 Tons

So you will need 3.41 Tons of air to cool just the machines so in this case a 4 ton unit should be fine.

Hope that clears stuff up.
full member
Activity: 686
Merit: 140
Linux FOREVER! Resistance is futile!!!
More air flow would probably help a lot.
You could use an evap cooler pulling air in from the outside, or less efficiently from the "hot" side of the room, blowing cooler air into the "cool" side.
If you had to, you could use an A/C unit to put SOME cold air into the intake air, just don't expect it to get the intake air WAY down on temp but it might help a little.



I already have a 24000 A/C in room (not in use for now), but dont know if it could help when we pull warm outside air to the room in the summer or not.

I was actually thinking about evap/water cooling air conditioners too, but doesn't high humidity cause problem to mining rigs?
I have some of those at home, they raise my home humidity from 30% in winter to +60% in the summer when they are in use.