Topic: Mining room cooling issue. (Read 2986 times)

full member
Activity: 210
Merit: 100
March 20, 2014, 07:32:09 PM
#43


either:
1) go to home depot and buy a 'whip' cord that has a plug matching your outlet and a 3-6' terminated wire lead. either wire these into a new outlet/housing or into a larger PDU capable of L6-30 or better socket.  There are distribution options that can handle 50A and allow you to wire into its terminals or splice to its cable
2) go to a specialty shop such as greybar or nedco and buy a big 50A locking outlet that is designed for industrial applications and then buy a sompatible server PDU.
[/quote]

I found out that the dryer socket is actually 30amps, which seems to be the standard in the US.  Upon speaking with other people I've decided that I can buy a 30amp pdu and hire an electrician to attach the right adapter for the outlet.  I will probably take that route if I decide to add the Antminer S2 to my mining collection.  I currently have 4 miners running on a 20amp and 2 more on the 15amp outlet; I took the time to actually figure out the exact amps of each outlet I was using, which is what I should have done before.  About to head to Home Depot right now to find a bigger vent scoop to place behind my Antminers.
legendary
Activity: 2128
Merit: 1005
ASIC Wannabe
March 20, 2014, 08:50:09 AM
#42
How do you convert the dryer's 240V to 120V?

Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.

I got ahead of myself and made a bad assumption; the socket that I am on is not 50amps, it is 15amps.  I made the assumption that because it was next to the dryer socket that they were on the same circuit but that was proven wrong when I tested the circuit breakers today.  I'm going to have to split up my Antminers and have them in different rooms so that I don't overload any one circuit.  I would like to utilized the actual dryer socket but as of right now, I don't know how.  I am much more safety conscious nowadays and am glad that I checked my circuit breakers.

either:
1) go to home depot and buy a 'whip' cord that has a plug matching your outlet and a 3-6' terminated wire lead. either wire these into a new outlet/housing or into a larger PDU capable of L6-30 or better socket.  There are distribution options that can handle 50A and allow you to wire into its terminals or splice to its cable
2) go to a specialty shop such as greybar or nedco and buy a big 50A locking outlet that is designed for industrial applications and then buy a sompatible server PDU.
donator
Activity: 1057
Merit: 1021
March 20, 2014, 08:33:11 AM
#41
Just wait until summer kicks in. 
hero member
Activity: 635
Merit: 500
March 20, 2014, 05:32:19 AM
#40
I have a fan for 22000 air m3/hour. Thats enough.

Smiley
hero member
Activity: 490
Merit: 500
March 19, 2014, 08:41:46 PM
#39
Haha, if you think the noise is going to be a problem wait until the room-mate gets their share of the electricity bill. Tongue

The answer is to turn your miners inside out and put larger quieter fans directly on the heatsinks then leave the door open.
Here's a video so you can see how quiet this makes them: http://www.youtube.com/watch?v=VOyrCut0y30


sr. member
Activity: 1316
Merit: 254
Sugars.zone | DatingFi - Earn for Posting
March 19, 2014, 01:30:55 AM
#38
Ok here's what you do since no one else has any better ideas besides killing or kicking out roommate lol !! I've set me up a few grow rooms for "friends" befor .. Buy a 6 inch can fan from your local hydro store . Also get the ducting and cut a hole in the ceiling in the room or closet. Keep the hole so you can put back the drywall if you ever need too. Have the fan pull the hot air from right behind the antminers..  This will solve your problem and the room will become half the temp it used to be ...  Good luck .........   A 4 inch one might also work for your purpose and use less power ...
I have a similar problem with heat/wife, I have a 6inch wall fan arriving shortly so I will update on its success after it arrives.

If you can get that ducting out ur window it saves on cutting your ceiling  Wink pvc ducting is cheap as chips, if you use foil, make sure its secured away from those miners.

Personally I would take the mummy route.. but what to do with the kids ?
full member
Activity: 210
Merit: 100
March 19, 2014, 01:02:11 AM
#37
How do you convert the dryer's 240V to 120V?

Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.

I got ahead of myself and made a bad assumption; the socket that I am on is not 50amps, it is 15amps.  I made the assumption that because it was next to the dryer socket that they were on the same circuit but that was proven wrong when I tested the circuit breakers today.  I'm going to have to split up my Antminers and have them in different rooms so that I don't overload any one circuit.  I would like to utilized the actual dryer socket but as of right now, I don't know how.  I am much more safety conscious nowadays and am glad that I checked my circuit breakers.
full member
Activity: 168
Merit: 100
March 19, 2014, 12:21:17 AM
#36
I bought a floor model portable ac unit from searsoutlet.com for $79.99. I had to fabricate my own exhaust hook up as it was missing. Cost me about $25 in parts at homedepot. I blow the cold ac through the intake fans. Problem is the damn thing uses 950w just for the AC. I will probably only use it in the summer when its 100+ degrees here in Texas.

sr. member
Activity: 420
Merit: 263
let's make a deal.
March 15, 2014, 12:31:52 AM
#35
i'm not using the 240v twist socket.  i'm one the socket next to the 240v socket. I believe this is the washer socket that is on the same 50amp circuit. If i am wrong about this, it would mean that the socket is run on the 40amp circuit meant for the kitchen, which is enough. My apt has a 50amp circuit for washer/dryer room, 40amps for kitchen, 20amps for living room, and 15amps for bedroom. If I decide to increase my mining operation to anything more than what I have now, I should probably hire an electrician.

By twist socket, do you mean a NEMA L15-30?  if so, you can get a power distribution module used for mobile film and theatrical production.  some modules have a pass-through plug to the dryer.

rack mount ftw. moar power



http://www.gearboxpro.com/rack-mount-power-distribution

AFAIK these connectors are rated to 30A so you may want to double check the ratings; washer may be on its own 20A circuit?

legendary
Activity: 1148
Merit: 1000
March 15, 2014, 12:18:37 AM
#34
Tell roommate you are getting rid of the miners to make room for your new hobby...beekeeping.
Leave web browser open with order for 10,000 bee 'starter kit'.

Profit.
full member
Activity: 210
Merit: 100
March 15, 2014, 12:10:47 AM
#33
i'm not using the 240v twist socket.  i'm one the socket next to the 240v socket. I believe this is the washer socket that is on the same 50amp circuit. If i am wrong about this, it would mean that the socket is run on the 40amp circuit meant for the kitchen, which is enough. My apt has a 50amp circuit for washer/dryer room, 40amps for kitchen, 20amps for living room, and 15amps for bedroom. If I decide to increase my mining operation to anything more than what I have now, I should probably hire an electrician.
hero member
Activity: 784
Merit: 1000
Live Stars - Adult Streaming Platform
March 14, 2014, 11:55:00 PM
#32
How do you convert the dryer's 240V to 120V?

Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.

Your power supplies will be more efficient on 240V, so stick with that.  You can switch out the receptacle for one that will mate with a 240V PDU twistlock connector.
but this will burn my machine because my machine is 120v
hero member
Activity: 630
Merit: 500
March 14, 2014, 11:11:54 PM
#31
How do you convert the dryer's 240V to 120V?

Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.

Your power supplies will be more efficient on 240V, so stick with that.  You can switch out the receptacle for one that will mate with a 240V PDU twistlock connector.
hero member
Activity: 784
Merit: 1000
Live Stars - Adult Streaming Platform
March 14, 2014, 10:00:02 PM
#30
How do you convert the dryer's 240V to 120V?

Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.
sr. member
Activity: 280
Merit: 250
March 14, 2014, 08:09:55 PM
#29
I have a room that is about 8'x8'x11' which serves as home to my 6 Antminer S1's.  The problem is that the room gets quite warm when door is shut.  If I leave the door open, I will most likely annoy my roommate with the noise.  Any way for me to keep my miners cool and not annoy my roommate?  I was thinking about cutting a hole at the bottom and top of the door but I wonder if that'll be enough.  If the room is very warm, it's obviously damaging to the miners right?  The room doesn't get hot enough to start a fire or anything(obviously) but it feels like the middle of summer when the rest of the apartment is cool.  I have my miners unplugged for the moment till I figure out a solution.  Smart inputs will be appreciated.

If you cut a hole in your door. The noise will also get out.
full member
Activity: 434
Merit: 105
March 14, 2014, 08:07:39 PM
#28
tell you room mate to get on board the train. feed him a little BTC watch his eyes get big and then show him how to buy a U2. then tell him how much more and how much faster you are able to mine. if all goes well and he takes the blue pill or the red pill or whichever on it is then it could snowball into a full blown mining operation and you guys rent another location to build your farm. BOOM business partners, mad cash flow, get the khakis, get the chicks and no more room mate. That was the goal right? Get rid of the room mate?

or you could be like bro i'll give you one percent to ignore all that noise.
full member
Activity: 210
Merit: 100
March 14, 2014, 07:47:02 PM
#27
Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.



I'm running the miners on the 50amp washer/dryer circuit.  No way would I run all 6 Antminer S1's on a 15amp circuit; it would probably trip the circuit breaker or start a fire.  I've read that 15amps can support 3 Antminers and 50amps support about 18.  I definitely did my research beforehand.
legendary
Activity: 1512
Merit: 1057
SpacePirate.io
March 14, 2014, 03:22:55 PM
#26
Likely your third problem is that you're going to be maxing out your 15A circuit too. My guess is that the next power supply you add is going to tip the load and trip your breaker.

As far as home cooling is concerned, you need to create airflow. If you can, open two windows and place two box fans into the windows. One bringing in air, the other as an exhaust fan pushing the hot air out. Also remember that cold air sinks and hot air rises.  To help the process, you can also put in insulated ducting from where your miner exhaust is and then the other end of the duct out the window. Another option is room-based AC unit, but you have to be careful with them. They usually have an condensation collector that fills up, they also pull moisture out of the air and static discharge will rise in the room. So don't touch your miners without some ESD protection.

The other option is to put the miners in a datacenter. Between the improvement costs you need to make and that you're probably going to run out of power, you may want to consider getting a cabinet. Lots of cold air, reliable power, and room to grow your farm.

hero member
Activity: 854
Merit: 500
March 14, 2014, 03:21:30 PM
#25
I have a room that is about 8'x8'x11' which serves as home to my 6 Antminer S1's.  The problem is that the room gets quite warm when door is shut.  If I leave the door open, I will most likely annoy my roommate with the noise.  Any way for me to keep my miners cool and not annoy my roommate?  I was thinking about cutting a hole at the bottom and top of the door but I wonder if that'll be enough.  If the room is very warm, it's obviously damaging to the miners right?  The room doesn't get hot enough to start a fire or anything(obviously) but it feels like the middle of summer when the rest of the apartment is cool.  I have my miners unplugged for the moment till I figure out a solution.  Smart inputs will be appreciated.

two ways:

1. Pull off those cheapo fans and spend some money on quiet fans to replace them.  Try http://www.quietpc.com/casefans

2. Convert them to water cooling.

full member
Activity: 210
Merit: 100
March 14, 2014, 02:54:43 PM
#24
ding, ding, ding!  just had a moment of realization.  I overlooked the obvious; the dryer room has a exhaust vent built-in for the dryer!  Shocked  I'll put a fan on the ceiling and run the duct work down to the dryer exhaust and voila! the hot air is removed from the room.  Thanks for all your inputs.