What determines if the line is 208/240/250 Volts. I looked at the NEMA 10-50 Socket again and noticed it says 250V. I assumed it was 208V since that seems to be what most PDUs reference. How do I know what voltage my line actually is? Should I go with what's written on the socket? Can the voltage be changed at the circuit breaker or do you need to have the building wired for different voltages?
Ah the ole 208V/220V/230V/240V/250V question.
So what is 208V?In the US the only place 208V exists is when tapping between two phases of a 3 phase circuit. Datacenters and industrial buildings will be supplied power using 3 phases where each line is 120V potential with the ground. Each line is out of phase from the other two. Tapping from one phase to another results in a 208V circuit. It allows more circuits to be installed on one wiring run (among other reasons).
All the rest of the power in the US is 120V/240V split phase where two 120V mains are supplied. Tapping between them gets you 240V. Tapping either of the 120V mains to the neutral gets you 120V. That is how homes in US can have both 120V and 240V using only 3 wires (leg1, leg2, and neutral) from the street.
If all that was confusing don't worry about it. The important part is that 208V circuits only exist in buildings wired for 3phase power.
The good news a PDU designed for 208V should work fine at 220V-240V. Some brands will even write it like that (208V/230V).The APC 30A models I listed above are designed for 208V circuits but work fine with 240V. The only thing to worry about would be a 3 phase 208V PDU. A PDU listed as 3 phase 208V is designed to take the ENTIRE 3 phase circuit (rather than split 3 phase circuit into 3x 1 phase circuits). Connecting that to non 3phase wiring would be very very bad. Good news is they use completely different plugs so you would have to try hard to get it connected.
So why do some things say 220V, some 230V, some say 240V? Stupidity? Voltage in the US is often called 110V/220V but it isn't. It is actually 115V/230V however it can vary from location to location and even on time of day.
Generally speaking:
220V/230V/240V all refer to the same thing.
110V/115V/120V all refer to the same thing.
You can't change your voltage (well not in any way that is useful). Your voltage depends not only on the building but the mains supplied by the power company. You got what you got.
So what is 250V?Nothing runs @ 250V the connectors are simply rated @ 250V. Which means it can safely handle 0V to 250V which covers 208V and 230V.