120V 20A = 1920W 120*20*0.8
Do you mean: 2400w
No. In the US a continual load can't use more than 80% of the circuits capacity. I just realized the 0.8 got changed into a smiley so I fixed that.
So in the US a 120V, 20A circuit is rated for 2400W PEAK however continual loads should not exceed 80% of that 2400W * 0.80 = 1920W.
Higher current = higher heat. House wiring is sized under the assumption that the load will vary and that is easier to cool. Now you "can" pull 2400W from a 20A breaker continually but that would be a violation of the NEC as the wire would be under greater resistance that intended for continual use and the breaker won't trip. In theory if the wiring was substandard, or faulty, or corroded due to age it "could" cause a fire. Now the risk is probably pretty low but the Electrical Code is designed to be conservative because it involves people's lives.
I have no knowledge of European standards, outlets, or ratings but current, resistance, heat are pretty much universal so the same general concepts still apply.
Does that mean on one socket i cant go above 1920w 2400w! Is there some kind of ettiqute in terms of leaving some cushion or can you go pedal to the medal and use all the juice it can give?
Other than the 20% derate for continual loads, yes. So the 1920W not the 2400W is the correct figure if you are running a load continually (like a 24/7 miner).
I take it this is for sockets in EU and not US, same with the connector on the pdu? ( NEMA L6-30R )
No. NEMA is Noth American Electrical Manuacturers Association. They are all US outlets. The NEMA 5-15 is the "standard" US wall outlet. The NEMA L6-30 is a 30A, 240V outlet which uses a locking connector.
Here is an example I just like the photo not trying to give this seller any business:
http://www.ebay.com/itm/APC-AP9571-1U-Rackmount-PDU-208V-24A-12-C13-Outlets-/261343426014?pt=US_Power_Distribution_Units&hash=item3cd94835deThere are tons and tons and tons of this PDU (PDU = fancy name for datacenter high current power strip). APC probably makes a couple millions so there are always used ones on ebay for cheap.
It has a NEMA L6-30P plug. The plug is rated for 30A but you will notice in the description it says 24A. Why? NEC requires that continual loads be derated 20%. 30A * 0.8 = 24A. 24A * 240V = 5760W.
Note the official specs are 208V because they were designed for datacenters but they work fine at 240V as well. It is simply a "power strip" with circuit breaker there are no electronics which require a specific voltage.
So:
30A breaker ------> 10 AWG wiring -------> NEMA L6-30R outlet ------> AP9571 (w/ L6-30P plug).
You now have 5760W of mining power, done right and safe. The PDU gives you 12 outlets so no matter how your rigs are configured you are good to go.
I ran 12KW of GPUs off three of these.