Pages:
Author

Topic: Gauging interest in a S5+ / 3xS7 specific power supply breakout board (Read 9804 times)

legendary
Activity: 1500
Merit: 1002
Mine Mine Mine
works with 2500bb with adjustable voltage ? i'd assume it should

I just checked it, and it doesn't. And I can't see anything that we can connect to make it work at first sight.
The internals are different between the 2000BB and the 2500BB. I'll have a look at a 1600BB if I still have one in stock, but it should be the same as 2000BB.

ah ha ! lucky i asked. but the pinput diagram "looks" the same between the 3 models.

will wait for you to check & see how it goes.

thx for checking it Wink
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
works with 2500bb with adjustable voltage ? i'd assume it should

I just checked it, and it doesn't. And I can't see anything that we can connect to make it work at first sight.
The internals are different between the 2000BB and the 2500BB. I'll have a look at a 1600BB if I still have one in stock, but it should be the same as 2000BB.

J4bberwock,

Can you get me PCI-e cords ASAP?

Just curious if you can.  I haven't ordered any from you yet... But I want to ASAP

EDIT:  YOU ROCK, MAN!!!!

THANKS!!!!!!
hero member
Activity: 840
Merit: 1000
works with 2500bb with adjustable voltage ? i'd assume it should

I just checked it, and it doesn't. And I can't see anything that we can connect to make it work at first sight.
The internals are different between the 2000BB and the 2500BB. I'll have a look at a 1600BB if I still have one in stock, but it should be the same as 2000BB.
legendary
Activity: 4326
Merit: 8950
'The right to privacy matters'
Thanks for the detailed and educational post on the meters, I had no idea. I used the same meter, though, to read the change from 227v to 240v. Also, my 227v reading went back up to 240v if I removed the load. The sag was caused by the power load and heat from summer. Winter temps are definitely helping right now.

No utility sets a transformer for 220v, they're all set to 240v. If by voltage coming into the neighbourhood you mean the top most wire bare (or 3 wires if 3 phase is available in your area) it's neither 240v nor 480v. In fact, quite far from it. Those lines run at 12200v or 14400v generally, and are transformed to 240v before they enter your property. When you read 208v on 3 phase, that's quite normal. 3 phase systems in the low volt range are 120v/208v, not 220v or 240v.

Oh, don't forget that your 1210w figure depends on a PSU with 93% efficiency. 2880w are no where near 93% efficient according to the tests I did. (measured DC output vs AC input) Not a good way to calculate your voltage.

What did your psu show  90% or less?
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
Thanks for the detailed and educational post on the meters, I had no idea. I used the same meter, though, to read the change from 227v to 240v. Also, my 227v reading went back up to 240v if I removed the load. The sag was caused by the power load and heat from summer. Winter temps are definitely helping right now.

No utility sets a transformer for 220v, they're all set to 240v. If by voltage coming into the neighbourhood you mean the top most wire bare (or 3 wires if 3 phase is available in your area) it's neither 240v nor 480v. In fact, quite far from it. Those lines run at 12200v or 14400v generally, and are transformed to 240v before they enter your property. When you read 208v on 3 phase, that's quite normal. 3 phase systems in the low volt range are 120v/208v, not 220v or 240v.

Oh, don't forget that your 1210w figure depends on a PSU with 93% efficiency. 2880w are no where near 93% efficient according to the tests I did. (measured DC output vs AC input) Not a good way to calculate your voltage.

Thanks for the reply.  Sounds interesting.  I'm wondering if the 220 I'm suspecting is after voltage drop across the 2880W PSU with a load on it when I do the math?
legendary
Activity: 1500
Merit: 1002
Mine Mine Mine
works with 2500bb with adjustable voltage ? i'd assume it should
hero member
Activity: 895
Merit: 504
I went ahead and ordered mine from finsky here in the US  Grin

How much was the total?
legendary
Activity: 1168
Merit: 1009
I went ahead and ordered mine from finsky here in the US  Grin
legendary
Activity: 1596
Merit: 1000
Thanks for the detailed and educational post on the meters, I had no idea. I used the same meter, though, to read the change from 227v to 240v. Also, my 227v reading went back up to 240v if I removed the load. The sag was caused by the power load and heat from summer. Winter temps are definitely helping right now.

No utility sets a transformer for 220v, they're all set to 240v. If by voltage coming into the neighbourhood you mean the top most wire bare (or 3 wires if 3 phase is available in your area) it's neither 240v nor 480v. In fact, quite far from it. Those lines run at 12200v or 14400v generally, and are transformed to 240v before they enter your property. When you read 208v on 3 phase, that's quite normal. 3 phase systems in the low volt range are 120v/208v, not 220v or 240v.

Oh, don't forget that your 1210w figure depends on a PSU with 93% efficiency. 2880w are no where near 93% efficient according to the tests I did. (measured DC output vs AC input) Not a good way to calculate your voltage.
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
Is there anyone powering 3 S7 with this? Which fan do you use / recommend for cooling the PSUs?

I am. My own contraption, but the same end result as j4bber's breakout board. His solution is just much more elegant. I'm using 2 Delta fans, approximately 150CFM each. Could get by with lesser fans, but I had these on hand so why not.

Sometimes, PDU's come into play.  For instance, my 30 amp PDU's have two 15 amp legs.  15 amps x 220 volts = 3,300 watts.  6,600 watts maximum with both 15 amp legs combined.

I'm presently using IBM 2880 PSU's to power 2 x S7's on each PSU.  1220 watts x 2 = 2440 watts.  I might use 2 x IBM 2880's and 1 x Corsair AX 860 on one 30 amp PDU to power 5 x S7's instead of using only 1 x IBM 2880 alone on each 15 amp leg of the 30 amp PDU.  However, more than likely, I will end up powering only 4 x S7's with 2 x IBM 2880's for each 30 amp PDU to remain well within the 75% allowed for each circuit.

I may probably go with this new setup J4bberwock has come up with once all of my IBM's are in use [22 x total IBM 2880's].  I would have the option to power 5 x S7's comfortably on one 30 amp PDU with 2 of these new setups of J4bberwock's [One for each 15 amp leg on the 30 amp switched PDU's].

Man, I can't even imagine the noise 22 of those would make.

Why are you only getting 220V from your service? Should be 240V. Mention that when the engineer comes by, he'll send a team of linesmen to increase voltage on the transformer in the pole. They bumped mine up after I complained about having only 227V with my heavy load.

It really depends on the meter you are using.  Most of the meters I use have an internal resistance of 10 million ohms or higher, which gives a 240 Volt reading.  If you use an old analog triplet model 310 meter with an internal resistance of 1 million ohms, you will see approximately 220 volts.  The less resistance the meter has internally when measuring voltage, the less voltage you will read.  The higher resistance internally inside the meter when measuring voltage, the higher voltage you will read.

Also, I'm reading 11 amps on a PDU that powers two S7's [Batch 1] with an IBM 2880W PSU.  If you multiply 220 Volts x 11 amps, you get 2,420 watts.  If you divide 2,420 watts by 2 S7's [Batch 1 @ 600 MHz), you get 1,210 watts.  How many watts were the S7 batch 1 clocked at 600 MHz rated?  Answer:  1,210 watts.

The internal resistance of ANY meter [When measuring voltage] is high.  However, some meters have higher resistance than others.  Some meters [Especially analog meters] have "ranges" you can select when measuring voltage and the internal resistance of the meter can vary depending on the range you have chosen.  The Triplet model 310 states on the meter it is 20,000 ohms per volt internal resistance.  If you put the meter in the 60 volt range, 60 x 20,000 = 1,200,000 ohms internal resistance.  

If you were in the 120 volt range, the internal resistance would be 120 x 20,000 = 2,400,000 ohms internal resistance.  If you were in the 300 volt range, the internal resistance of the meter would be 300 x 20,000 = 6,000,000 ohms.  Which see:




The previous internal resistance when measure voltage concerned measuring DC Volts with a Triplet model 310 analog meter.  When measuring AC Volts with the model 310, it's internal resistance is 15,000 ohms per volt.  Which see:




If you were in the 300 volt range with a Triplet model 310 measuring what you may think is a 240 volt circuit, you would see approximately 230 to 233 volts because it has 4,500,000 ohms internal resistance in the 300 volt range (300 x 15,000 ohms per volt AC).  If you used a Fluke digital meter with an internal resistance of approximately 8,000,000 ohms to measure voltage on a 240 volt AC circuit, you would see approximately 240 volts.  The internal resistance of a meter when measuring AC Volts is generally a little bit lower than the internal resistance of the same meter when measuring DC Volts.  However, they are both (AC and DC) still quite high.

I do not doubt you read too low of voltage at 227 volts with your meter.  The power company can adjust the voltage output on most transformers.  All I'm saying is the amount of voltage one reads can vary by what meter they use.  Especially, if they switch from an analog to digital meter or vice versa.  

If you look back at my previous statement about the 11 amps reading on my PDU, that will tell you my voltage in my home is 220 volts when you compare it to how many watts 2 x batch 1 S7's will consume when set at default of 600 MHz [1,210 watts each for a total of 2,420 watts].  I've seen a lot of 3 Phase voltages read 208 volts.  Does this mean the voltage is too low?  No, that 208 volts would be read with an analog meter with a lower internal resistance than a digital meter set to a higher internal resistance that reads about 215 volts.

Many people who work with electronics on an everyday basis will tell you they are careful about what meter they use when measuring voltage on a low voltage circuit verses a high voltage circuit.  It can make a big difference.  Especially, with low voltages.

I think you know I'm getting a power upgrade here at my house soon from 200 amps to 600 amps [or at least 500 amps].  I'm going to ask the engineer [When he arrives in the next few days] what the line voltage is on each phase coming into the neighborhood.  It's very possible the line voltage is 240 volts or 480 volts and the transformer is stepping it down to 220 volts instead of 240 volts.  If they in fact have 240 or 480 to start with before knocking it down to 220, I'm going to ask for a transformer  that knocks it down to 240 instead of 220.  It may be they have a transformer they can install to adjust the voltage output to 240 for me.  Many transformers have that capability depending on where they terminate the feeder cable on the coils in the transformer.

Again, the reason I believe my voltage is actually 220 volts is because of the amp reading I'm getting on my PDU with 2 x S7's that are batch 1 and set at 600 MHz.  They are supposed to burn 1,210 watts each at the wall.  Two of them would be 2,420 watts at the wall.  If we divide 2,420 watts by the 11 amps I'm reading on the PDU, it equals 220 Volts.  I'm definitely asking them if they will increase it to 240 volts when they install a new transformer.
legendary
Activity: 1596
Merit: 1000
Is there anyone powering 3 S7 with this? Which fan do you use / recommend for cooling the PSUs?

I am. My own contraption, but the same end result as j4bber's breakout board. His solution is just much more elegant. I'm using 2 Delta fans, approximately 150CFM each. Could get by with lesser fans, but I had these on hand so why not.

Sometimes, PDU's come into play.  For instance, my 30 amp PDU's have two 15 amp legs.  15 amps x 220 volts = 3,300 watts.  6,600 watts maximum with both 15 amp legs combined.

I'm presently using IBM 2880 PSU's to power 2 x S7's on each PSU.  1220 watts x 2 = 2440 watts.  I might use 2 x IBM 2880's and 1 x Corsair AX 860 on one 30 amp PDU to power 5 x S7's instead of using only 1 x IBM 2880 alone on each 15 amp leg of the 30 amp PDU.  However, more than likely, I will end up powering only 4 x S7's with 2 x IBM 2880's for each 30 amp PDU to remain well within the 75% allowed for each circuit.

I may probably go with this new setup J4bberwock has come up with once all of my IBM's are in use [22 x total IBM 2880's].  I would have the option to power 5 x S7's comfortably on one 30 amp PDU with 2 of these new setups of J4bberwock's [One for each 15 amp leg on the 30 amp switched PDU's].

Man, I can't even imagine the noise 22 of those would make.

Why are you only getting 220V from your service? Should be 240V. Mention that when the engineer comes by, he'll send a team of linesmen to increase voltage on the transformer in the pole. They bumped mine up after I complained about having only 227V with my heavy load.
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
Is there anyone powering 3 S7 with this? Which fan do you use / recommend for cooling the PSUs?

I am. My own contraption, but the same end result as j4bber's breakout board. His solution is just much more elegant. I'm using 2 Delta fans, approximately 150CFM each. Could get by with lesser fans, but I had these on hand so why not.

Sometimes, PDU's come into play.  For instance, my 30 amp PDU's have two 15 amp legs.  15 amps x 220 volts = 3,300 watts.  6,600 watts maximum with both 15 amp legs combined.

I'm presently using IBM 2880 PSU's to power 2 x S7's on each PSU.  1220 watts x 2 = 2440 watts.  I might use 2 x IBM 2880's and 1 x Corsair AX 860 on one 30 amp PDU to power 5 x S7's instead of using only 1 x IBM 2880 alone on each 15 amp leg of the 30 amp PDU.  However, more than likely, I will end up powering only 4 x S7's with 2 x IBM 2880's for each 30 amp PDU to remain well within the 75% allowed for each circuit.

I may probably go with this new setup J4bberwock has come up with once all of my IBM's are in use [22 x total IBM 2880's].  I would have the option to power 5 x S7's comfortably on one 30 amp PDU with 2 of these new setups of J4bberwock's [One for each 15 amp leg on the 30 amp switched PDU's].
legendary
Activity: 1596
Merit: 1000
Is there anyone powering 3 S7 with this? Which fan do you use / recommend for cooling the PSUs?

I am. My own contraption, but the same end result as j4bber's breakout board. His solution is just much more elegant. I'm using 2 Delta fans, approximately 150CFM each. Could get by with lesser fans, but I had these on hand so why not.
legendary
Activity: 1405
Merit: 1001
Is there anyone powering 3 S7 with this? Which fan do you use / recommend for cooling the PSUs?
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
Hey Dwardjr i have a few of J4bberworks break out boards best thng going right now i like how we can plug into PCEI plug to plug . Smiley . just bought one of his 2000 blade center boards, not this one, they are very nice. .

Agreed.

J4bberwocks HW is the shiznit!
legendary
Activity: 1274
Merit: 1000
Hey Dwardjr i have a few of J4bberworks break out boards best thng going right now i like how we can plug into PCEI plug to plug . Smiley . just bought one of his 2000 blade center boards, not this one, they are very nice. .
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
J4bberwock,

Its been a while since I've read this forum.  What I'm about to ask may have already been asked:

Do you have anything in the works for something similar but with IBM 2880W PSU's?  It might be worth coming up with something to control the voltage on the 2880 and have a digital meter for it's output voltage.

I have a little over 20 x IBM 2880's at my disposal with your breakout boards.  I may invest in your setup for this present design in the future [Once all of my 2880's are in use].



Hi, I've probed the 2880w PSU for voltage control pins, and it's not easy to move it from 12v. I still need to try one easy trick just in case it'd work.

The only practical way someone found until now is to use an arduino to reprogram on the fly the internal ROM of the PSU to allow different voltage outputs.

http://www.rcgroups.com/forums/showpost.php?p=30428005&postcount=2972

The same thing can probably be done to output lower voltages, but it's a bit overkill just to allow us to go from 11v to 13v

Okay,

Thanks for the reply, Sir.

EDIT:  After reading the link, I must agree...  It's overkill.
hero member
Activity: 840
Merit: 1000
J4bberwock,

Its been a while since I've read this forum.  What I'm about to ask may have already been asked:

Do you have anything in the works for something similar but with IBM 2880W PSU's?  It might be worth coming up with something to control the voltage on the 2880 and have a digital meter for it's output voltage.

I have a little over 20 x IBM 2880's at my disposal with your breakout boards.  I may invest in your setup for this present design in the future [Once all of my 2880's are in use].



Hi, I've probed the 2880w PSU for voltage control pins, and it's not easy to move it from 12v. I still need to try one easy trick just in case it'd work.

The only practical way someone found until now is to use an arduino to reprogram on the fly the internal ROM of the PSU to allow different voltage outputs.

http://www.rcgroups.com/forums/showpost.php?p=30428005&postcount=2972

The same thing can probably be done to output lower voltages, but it's a bit overkill just to allow us to go from 11v to 13v
legendary
Activity: 1302
Merit: 1318
Technical Analyst/Trader
J4bberwock,

Its been a while since I've read this forum.  What I'm about to ask may have already been asked:

Do you have anything in the works for something similar but with IBM 2880W PSU's?  It might be worth coming up with something to control the voltage on the 2880 and have a digital meter for it's output voltage.

I have a little over 20 x IBM 2880's at my disposal with your breakout boards.  I may invest in your setup for this present design in the future [Once all of my 2880's are in use].

legendary
Activity: 4326
Merit: 8950
'The right to privacy matters'

If you want to easily have the voltage adjust working, ask them if they can ship you revision number lower than S9M.

If they can't, you could use some zero ohm resistors to mod according to my pictures a few posts ago. I used pins salvaged from dead DPS2000 PSUs on mine.
Those resistors should do the job if the leg diameter isn't too big (looks ok on the picture, and some people used actual cut legs from resistors soldered together to replace the pins):
Ebay item 201428019892
Ebay item 121097959648

Just to be safe, I'd put them in some heat shrink tube in case the actual resistor body could touch another pin.

If you don't have an hot air station and a solder sucker, you can even carefully drill with a 0.7-0.8mm drill bit in the center of the solder pad that is missing the pin.

Total length of the pins is 42mm. I haven't been able to source them from regular sources like digikey/mouser...
Will try from my main connectors supplier.


they read s7.

  I have your 2x board on hand  I will post assembly > when all pieces come on hand.
Pages: