d57heinz - this was one of the EXACT sources I used in determining my electrical needs. If you look further you'll find the EXACT same thing being said in dozens of electrician forums on the internet.
I'm not claiming to be an electrician as are some, but I think the confusion comes from the fact that the 2 poles are 180 degrees out of phase and thus the MAIN does not see 340A simultaneously, but 170A on leg 1 with one phase and 170A on leg2 during the different phase. This is essentially the same as 240V - using 2 x 120V out of phase connections to achieve the 240V.
I can also concur that I'm utilizing 32000 watts sustained currently - majority on 120V - divided among the 2 poles/legs. Fluctuations go up to 38000 watts during use of misc items like washer/microwave/gaming machine/hot water heater/air compressor etc..
I did not mean for it to be taken that you can draw 340 amps ON BOTH LEGS SIMULTANEOUSLY. Yes, there are 200 amps available on both legs. Yes, one can draw 200 amps on one pole (leg) in the main panel depending on how many Ohms of resistance is in the load. However, one cannot DRAW 200 amps of both legs simultaneously (400 Amps). The 200 amp breaker would trip well before that would happen.
You said in a previous post:
Well, I guess my farm is defying all logic then.
I'm certainly pulling in over 200A total - all using 120V.
This is not possible on a 200 amp main service panel with a 200 amp main breaker. Yes, there is 200 amps "available" on each pole [That some call legs] but a 200 amp breaker would not allow more than 5% of 200 amps in most cases. So, even though there is 400 amps total available on both poles combined, a 200 amp main breaker will not allow for more than a 200 amp load to flow.
Yes, I've said I'm an electrician. However, I have also said I'm not a "certified" electrician. I quit taking my night courses for master electrician just shy of taking the test to become a "journeyman" electrician. I was an "apprentice" [Gaining experience] while taking night courses for almost 3 years. In order for one to take the journeyman test and/or the master electrician test, they must have a certain number of hours (experience) in the field before being allowed. I've said in many posts throughout bitcointalk.org that I'm not a "certified" master electrician.
I'm not here to argue, Sir. I prefer to keep this civilized. You said you are putting a load of 32,000 watts on your 200 amp panel with most of it on 120 Volts. If we do the math, that is a conflicting statement to the statement you made earlier. Which see:
Well, I guess my farm is defying all logic then.
I'm certainly pulling in over 200A total - all using 120V.
You said you are pulling (drawing) OVER 200 A total. If that's the case, you are pulling (drawing) more than 24,000 watts with all of it using 120 Volts. So, "all using 120V?" One statement says "most" of it on 120V and another saying, "all" of it on 120. Which is it?
If you were pulling 32,000 watts with "all" on 120 Volts [32,000 watts divided by 120 volts = 266 amps] that would defy logic of having a 200 amp breaker. If you insist on saying you're pulling more than 200 amps through a 200 amp breaker, be my guest. I'm not going to try to convince you otherwise. However, if you believe the very link you said you went to, then listen to the last quote in that link if you don't want to listen to me:
You have too many conflicting statements, Sir. It's so confusing that I don't know what you are trying to imply anymore. It's just not possible to pull 32,000 watts at 120 volts (266 amps) through a 200 amp breaker UNLESS the breaker is defective.